1)

A water cooler of storage capacity 120 litres can cool water at a constant rate of P watts. In a closed circulation system (as shown schematically in the figure), the water from the cooler is used to cool an external device that generates constantly 3 kW of heat (thermal load). The temperature of water fed into the device cannot exceed 300C and the entire stored 120 litres of water is initially cooled to 100C . The entire system is thermally insulated. The minimum value of P (in watts) for which the device can be operated for 3 hours is

412021701_3q.JPG

(Specific heat of water is 4.2kJ kg-1 K-1 and the density of water is l000kg m-3 

 

 


A) 1600

B) 2067

C) 2533

D) 3933

Answer:

Option B

Explanation:

 Heat generated in device in 3 h = Time x power

= 3×3600×3×103

=324×105J

Heat used to heat water = msΔθ

= 120×l×4.2×103×20

Heat absorbed by coolant

Pt = 324×105120×l×4.2×103×20J

Pt = (325100.8)×105J

=223.2×105

P=223.2×1053600

=2067 W